any plumbers or mechanical engineers on here?

I need help sizing a gas line for some air make-up units. I have tried the online calculators but they didnt seem right. At least I hope they werent. If someone knows how to do this I will give more info. Any help would be appreciated. Thanks, Bob

Report this post to a moderator | IP: Logged

Old Post 09-13-2012 09:04 PM
Bob Klaus is offline Click Here to See the Profile for Bob Klaus Click here to Send Bob Klaus a Private Message Click Here to Email Bob Klaus Find more posts by Bob Klaus Add Bob Klaus to your buddy list Edit/Delete Message Reply w/Quote
Bill Rader
Banned

Registered: Jan 2010
Location: S.W. Ohio.
Posts: 248

more detail

Make up air for climate control? {air handler} ?
Need more info?

__________________
BILL RADER
CH HARDTIME HILLBILLY RODEO
HARDTIME HILLBILLY VOODOO

Report this post to a moderator | IP: Logged

Old Post 09-13-2012 09:37 PM
Bill Rader is offline Click Here to See the Profile for Bill Rader Click here to Send Bill Rader a Private Message Click Here to Email Bill Rader Find more posts by Bill Rader Add Bill Rader to your buddy list Edit/Delete Message Reply w/Quote
Bob Klaus
UKC Forum Member

Registered: Mar 2004
Location: Cincinnati, Iowa
Posts: 42

The place i work at is expanding into a new building. We are installing three heated air make-up units for two paint booths. We are also putting in radiant heaters. The gas pressure into the building is regulated to 5lbs. The total BTU for everything is 7.2 million. The length of the main trunk line will be about 250ft.

Report this post to a moderator | IP: Logged

Old Post 09-13-2012 09:49 PM
Bob Klaus is offline Click Here to See the Profile for Bob Klaus Click here to Send Bob Klaus a Private Message Click Here to Email Bob Klaus Find more posts by Bob Klaus Add Bob Klaus to your buddy list Edit/Delete Message Reply w/Quote
J Ternes
UKC Forum Member

Registered: Nov 2009
Location: Kansas
Posts: 98

Gas

Your pressure will need to be brought way down before the unit tie in, more than likely. Do this as close to the units as you can, because after the pressure is brought down to operating presure the distance from the unit will determine the size of your pipe. Meaning, the farther the trunckline is from the unit the bigger your feeder pipe must be, this is determined by the BTU's as well. If you wont call a local plumber or fuel gas tech, who ever is certified to do this in your area, at least call your gas company. Most will come out for free and take a look. I know 5 lbs dont sound like much pressure but it is! Its a high pressure line and if its not installed and regulated properly very bad things will happen. Most units run with onces of pressure not pounds This is why sizing and pressure regulating is so very important in commercial applications like this. You dont want to under regulate and get people hurt.

Report this post to a moderator | IP: Logged

Old Post 09-14-2012 03:02 AM
J Ternes is offline Click Here to See the Profile for J Ternes Click here to Send J Ternes a Private Message Click Here to Email J Ternes Find more posts by J Ternes Add J Ternes to your buddy list Edit/Delete Message Reply w/Quote
Bob Klaus
UKC Forum Member

Registered: Mar 2004
Location: Cincinnati, Iowa
Posts: 42

I totally understand what you are saying. There is nothing I would like more than to have this contracted out. I am an electrician, not a plumber. But with the way the economy is and the way my bosses are(tighter than a frogs a$$) they want to do it in house. I have no choice in the matter about where the equipment is located in relationship to the meter. It is already set. The trunk line will have to be 250 feet. The meter set is regulated at 5lbs, and I know this is considered high pressure. The local utilities will not recommend a pipe size. Neither will the contrators I have spoken with. If they are not doing the work they will not engineer the system, and I dont blame them a bit. I would feel the same way if if someone wanted me to design a 2500amp electrical service and not do the work. We have to get the system inspected and certified before the utilities will turn on the service. They have no problem with us doing the work in house, we have before. Just not a system this large. I was hoping someone could help me out with the calculations. I know I am looking at probley a 2 1/2" to 3" trunk line, maybe larger. I will figure something out. Thanks anyway, Bob

Report this post to a moderator | IP: Logged

Old Post 09-14-2012 05:01 AM
Bob Klaus is offline Click Here to See the Profile for Bob Klaus Click here to Send Bob Klaus a Private Message Click Here to Email Bob Klaus Find more posts by Bob Klaus Add Bob Klaus to your buddy list Edit/Delete Message Reply w/Quote
Little
UKC Forum Member

Registered: Jun 2003
Location: NC
Posts: 175

2" sch 40 BI for 5 psi natural gas is good for 13 MBTU at 250'.

Report this post to a moderator | IP: Logged

Old Post 09-14-2012 06:25 PM
Little is offline Click Here to See the Profile for Little Click Here to Email Little Find more posts by Little Add Little to your buddy list Edit/Delete Message Reply w/Quote
Bar M
UKC Forum Member

Registered: Dec 2011
Location: Texas
Posts: 74

quote:
Originally posted by Bob Klaus
The place i work at is expanding into a new building. We are installing three heated air make-up units for two paint booths. We are also putting in radiant heaters. The gas pressure into the building is regulated to 5lbs. The total BTU for everything is 7.2 million. The length of the main trunk line will be about 250ft.
7.2 million BTU is a lot. I work for a Natural Gas company and install meters. Run 2 inch iron black gas pipe up to the paint booths and come off from a 2 inch trunk line and reduce down to 1 inch for the over head htrs. You need to check what the paint booths inlet pressure calls for. Normally it 4 oz or 7 inches water column but some require more. If thats the case you can send in 5 pounds and regulate right before the inlet on the paint booths. Good luck.

Report this post to a moderator | IP: Logged

Old Post 09-14-2012 10:09 PM
Bar M is offline Click Here to See the Profile for Bar M Click here to Send Bar M a Private Message Find more posts by Bar M Add Bar M to your buddy list Edit/Delete Message Reply w/Quote
Bob Klaus
UKC Forum Member

Registered: Mar 2004
Location: Cincinnati, Iowa
Posts: 42

Sorry i have not responded sooner. Thanks guys. That was exacly what i needed. I was hoping we could get by with 2" black pipe. But I still aint looking foward to installing it. Thanks again, bob

Report this post to a moderator | IP: Logged

Old Post 09-18-2012 03:50 AM
Bob Klaus is offline Click Here to See the Profile for Bob Klaus Click here to Send Bob Klaus a Private Message Click Here to Email Bob Klaus Find more posts by Bob Klaus Add Bob Klaus to your buddy list Edit/Delete Message Reply w/Quote
Jason Gillespie
UKC Forum Member

Registered: Feb 2010
Location: Marion,Ind
Posts: 1641

2 in is fine for the 250 at 5lbs !Be sure to install drip legs at every unit to ensure moisture and condensation isnt blow in to units at time of power up!

__________________
Strike em When they strike Tree em When they tree! Call them as they are!

Lay-Up Kennels !!!!!!
Jason Gillespie
Marion , Indiana
(765)517-1591

*PAST AND PRESENT HOUNDS*

Ch NiteCh Gillespie's Lay-Up Lizzy R.I.P (Best reproducing female I have had in my Kennel) Produced 2 World Champions Hardwood Minnie & Spring Creek Pen-e-trator (Wave).

NSD World NiteCh NSD GrniteCh Ohio State CH UKC Grnitech PR'Gillespie's Hardwood Minnie (Lucky X's Lizzy)$KC ($114)
-2015 Mini Slam Final 4
-2016 Mini Slam Final 4
-2017 Mini Slam Final 4 (Grand Masters Qualified)Semi-Finalist
-2018 Mini Slam Final 4 (Grand Masters Qualified)
AO Slam Event Triple cast winner.2016
AO Night Hunt cast winner 2016.
2016 NSD Ohio State Champion.
2016 NSD Indiana State Ch 3rd place.
NSD GrniteCh
2016 Grand Masters Semi Finalist.

NSD World Nitech NSD Grnitech Ind State Ch UKC Grnitech Lay-Up's Spring Creek PEN-E-TRATOR A.K.A (WAVE) ( Grandson to SC Rock! Shows Rock 4xs in a 5 gen) ONLY LIVING GRNITECH GRANDSON TO SPRING CREEK ROCK ALIVE !!!!!!!!!!
2017 AO 9th Place Reg.
2017 NSD Indiana State NiteCh
2018 TW days 9th Place Reg.
2018 NSD World NiteCh
UKC Grnitech
NSD Grnitech
2019 AO Grand 16.

PR'Gillespie's Hardwood Ugg
PR'Gillespie's Hardwood Roxy
PR' Spring Creek Troopie

"Hunt them alone , if you want to take a Coondawg Home"

*Semen Stored @ Shultz Clinic in Michigan*
PRESERVATION FOR GENERATIONS !!!!

(RIP) Grnitech GrCh Hillbilly's Smoken Ringo Star HTX (Stud Fee $500)

Grnitech Taylors Lucky (Son of Henry Not for sale)

Grnitech Hardwood Patch (Not for Sale)

NSD WLDNITECH GRNITECH UKC GRNITECH PR' Lay-Ups Spring Creek PEN-E-TRATOR DNA-P ( Direct Grandson of SPRING CREEK ROCK!!!!)

PR'Gillespie's Lay-Up Lil Lucky (RIP)

Grnitech Stone Mountain Bronco

NiteCh PR'Hardwood Blackjack (Patch Son)

Report this post to a moderator | IP: Logged

Old Post 09-19-2012 12:11 PM
Jason Gillespie is offline Click Here to See the Profile for Jason Gillespie Click here to Send Jason Gillespie a Private Message Click Here to Email Jason Gillespie Find more posts by Jason Gillespie Add Jason Gillespie to your buddy list Edit/Delete Message Reply w/Quote
All times are GMT. The time now is 11:03 PM. Post New Thread    Post A Reply
  Last Thread   Next Thread
Show Printable Version | Email this Page | Subscribe to this Thread


Forum Jump:
 

Forum Rules:
You may not post new threads
You may not post replies
You may not edit your posts
HTML code is OFF
vB code is ON
Smilies are ON
[IMG] code is ON
 
< Contact Us - United Kennel Club >

Copyright 2003-2020, United Kennel Club
Powered by: vBulletin Version 2.3.0
(vBulletin courtesy Jelsoft Enterprises Limited.)